General requirements for routine laboratory access planning
1. The minimum distance between the central counter and the side counter aisle is 1.2 meters. 2. The minimum distance between the central counter and the central counter aisle is 1.5 meters. 3. The minimum distance between the central counter and the tall cabinet aisle is 1 meter. 4. The width of the central counter facing the wall should not be less than 1 meter. 5. The minimum distance between the two side counters aisle is 1.2 meters. 6. The aisle between two seats should not be less than 1.5 meters. 7. The distance between the seats and the central counter should not be less than 2 meters. 8. The aisle for the ventilation cabinet facing the wall is 1.8 meters. 9. The minimum distance between the ventilation cabinet and the experimental counter is 1.8 meters. 10. The recommended distance between two ventilation cabinets is 3 meters.